What is the overload current for a motor with the nameplate information 230 Volt, 3-phase, 7.5 HP, and 19 Amps?

Study for the Independent Electrical Contractors IEC Year 3 Test. Utilize multiple choice questions, each with hints and explanations. Boost your readiness and confidence for the exam!

To determine the overload current for a motor, you typically refer to the nameplate data, which includes the voltage, phase, horsepower rating, and full-load current. In this case, you have a three-phase motor rated at 7.5 HP and a nameplate full-load current of 19 Amps.

When calculating the overload current, a common practice is to use the National Electrical Code (NEC) guidelines, which often stipulate that overload protection should be set at 125% of the motor's full-load current for proper safeguarding against motor overheating.

To find the overload current, you can multiply the full-load current by 125%:

  1. Start with the full-load current: 19 Amps.

  2. Convert 125% to a decimal: 1.25.

  3. Calculate the overload current: 19 Amps x 1.25 = 23.75 Amps.

This calculation shows that the overload current, based on the given nameplate information and following the appropriate guidelines, is indeed 23.75 Amps. Thus, this result aligns perfectly with the provided choice, confirming its correctness.