For a feeder supplying one 5 hp and three 2 hp motors, what is the minimum size conductor allowed?

Study for the Independent Electrical Contractors IEC Year 3 Test. Utilize multiple choice questions, each with hints and explanations. Boost your readiness and confidence for the exam!

To determine the minimum size conductor needed for a feeder supplying one 5 hp and three 2 hp motors, it's essential to calculate the total load in amperes and then refer to the appropriate NEC (National Electrical Code) tables to select the correct conductor size.

First, convert the horsepower to kilowatts using the formula:

  • 1 hp ≈ 0.746 kW.

Thus:

  • The total load for the motors can be calculated:

  • One 5 hp motor: 5 hp × 0.746 kW/hp = 3.73 kW.

  • Three 2 hp motors: 3 × (2 hp × 0.746 kW/hp) = 3 × 1.492 kW = 4.476 kW.

Now, add the power of all motors:

  • 3.73 kW + 4.476 kW = 8.206 kW.

Next, to convert the total power (in kW) to amperes, use the following formula assuming a 480 V system (for example):

  • Amperes = Watts / Volts.

  • Total watts = 8.206 kW × 1000 = 8206